In f5 i2800, we can see the hardwired failover port .
Hi divyaskumar,
you may read the following solution article to see the pros & cons of each method...
https://support.f5.com/csp/article/K2397
In general a Hardwired Failover (with additional Network Failover configuration) is the recommended choice, since the Hardwired Failover supports a faster/better detection. The only downside of a Hardwired Failover is, that it requires you to place the individual units side-by-side in the same rack / fire compartment (max. 50 feet distance is supported).
Note: If you're running out of dedicated interfaces for the Network Failover configuration, then you can also use the INT/EXT production interface (e.g. via an additional VLAN) to establish the Network Failover communication. Well, its not a recommended practise to deploy an intermediate switch into Network Failover communication, but its still a supported scenario and has just very little downsides in combination with a Hardwired Failover setup. In this case the Active/Passive detection takes place over (very stable) Hardwired connection and the remaining stuff (e.g. Informational status exchange) takes place over the (potential unstable) Network Failover connection^^
Cheers, Kai