jfrizzell_43066's avatar
jfrizzell_43066
Apr 01, 2011
F5 LTM VIP/STP Problem
We are currently experiencing an issue in our data center. We have two F5 LTM’s with VIPs for our database cluster and webservers. In the data center, we run HP ProLiant Servers with Fault Tolerant Load Balancing (TLB) NIC teams and two Cisco 3560E switches with Etherchannel Layer 2 trunks. We have two F5 LTMs that are currently in an Active/Standby configuration. On the first LTM, we have interface 1.1 going to switch 1 and interface 1.2 going to switch 2. On the second LTM, we have the same configuration. Please see the simplified topology concerning the connection to the switches.
Over the weekend, we removed foundry switches and replaced those with the Cisco 3560E’s. Since this change over we have had a few issues with no resolution to date. First, when we try to access the VIP for our webservers on the F5 LTM by HTTP/HTTPS it does not resolve. If we try to access the LTMs HTTPS web address, it does not resolve either. However, we can access all servers using their physical address with HTTP/HTTPS. What is really weird is that we can ping the VIP and LTM address. We do not currently have an access-list on any device denying this traffic. Also, when we removed a NIC from the team, we could resolve the VIP and LTM by HTTP/HTTPs. The second issue is that spanning-tree is blocking the redundant interfaces on our second switch. Not sure why this is happening if the LTM is in an Active/Standby state and it must be noted that we are using STP pass through.
Hopefully someone reading this has experienced this before or has an idea/suggestion for a resolution. We have opened a ticket with F5, but no resolution yet. We opened a case with Cisco TAC and they have reviewed the switch configuration and everything looks good.
  • Found this thread useful, so posting our solution to it, not sure if there is some other way of doing it.
    Our problem was HP blade servers configured with TLB teaming initiating connections to a VIP where the F5 and HP servers were on the same VLAN - sometimes it worked, sometimes it didn't. Packet capture showed F5 sending traffic back to source MAC in request, rather than the MAC in the ARP table.
    Our solution: On the VIP, we set "Auto Last Hop" to "disabled", which fixed our problem on that VLAN. It actually broke connections coming in via another VLAN through a firewall, so we just configured another VIP on that VLAN. So ended up with 2 VIPs, with same IP, with different source vlans and different "auto last hop" settings.
    • Amitabha_118500's avatar
      Amitabha_118500
      We ran into this exact same issues months ago and running into it again now. We ended up disabling the fault tolerance on the server and didn't what was the root cause. stevehuffy 's comment explains it. Thanks A LOT. Namo Amituofo.....
  • It actually broke connections coming in via another VLAN through a firewall, so we just configured another VIP on that VLAN. So ended up with 2 VIPs, with same IP, with different source vlans and different "auto last hop" settings.
    may auto lasthop setting on vlan object be useful?
    sol13876: Overview of the Auto Last Hop setting (11.x)
    http://support.f5.com/kb/en-us/solutions/public/13000/800/sol13876.html
  • Hi Experts
    I have a similar issue in which after giving MAC masquerade address in traffic group 1, the Cisco Catalyst switch towards the ingress port doesn't learn it in ARP table. However, when I remove this configuration from the F5, it works fine on physical MAC of the active F5 interface.
    Anything to suspect on Cisco Catalyst IOS?
    Regards,
    Sumanta.
  • Just wanted to add my $.02. We are migrating from Cisco ACE to F5's. Mix of Viprion's and appliances. Running 11.6.1 HF1. Have had two cases now where a week plus after converting apps over to F5 (F5 is the layer 3 gw for the servers btw), they started having performance problems. Seemed to be only physical servers, with multiple nics and using teaming (HP servers).
    I noticed that servers that were working fine must have been configured for NFT (use only one nic at a time) because their mac never changed, and they had no issues. Servers that were using multiple nics simultaneously, had problems.
    Found this thread and disabled auto last hop on the server side vlan only and it immediately resolved the issue.
    Thanks everyone.